Rückmeldungen Beta 1.9.267

Fragen zur Nutzung, Features, usw..
ama
Beiträge: 70
Registriert: So Okt 14, 2018 7:38 pm

Re: Rückmeldungen Beta 1.9.267

Beitrag von ama »

Moin, Debug Level 2 - Infos zum Victron Fehler.

Code: Alles auswählen

2022-06-02 07:59:53: PID: 2464: legacy run server: Completed running command in 0.02s: ["modules.victron.device","bat","192.168.178.46"]

modules.common.fault_state.FaultState: ("modules.common.modbus <class 'struct.error'> required argument is not an integer", <FaultStateLevel.ERROR: 2>)
str(e)) from e
File "/var/www/html/openWB/packages/modules/common/modbus.py", line 105, in __read_registers
self.delegate.read_holding_registers, address, types, byteorder, wordorder, **kwargs
File "/var/www/html/openWB/packages/modules/common/modbus.py", line 123, in read_holding_registers
power = self.__tcp_client.read_holding_registers(842, ModbusDataType.INT_16, unit=modbus_id)
File "/var/www/html/openWB/packages/modules/victron/bat.py", line 34, in update
self.components[component].update()
File "/var/www/html/openWB/packages/modules/victron/device.py", line 60, in update
Traceback (most recent call last):

The above exception was the direct cause of the following exception:

struct.error: required argument is not an integer
message.function_code)
File "/usr/local/lib/python3.5/dist-packages/pymodbus/framer/socket_framer.py", line 212, in buildPacket
packet = self.client.framer.buildPacket(packet)
File "/usr/local/lib/python3.5/dist-packages/pymodbus/transaction.py", line 228, in _transact
broadcast=broadcast
File "/usr/local/lib/python3.5/dist-packages/pymodbus/transaction.py", line 158, in execute
return self.transaction.execute(request)
File "/usr/local/lib/python3.5/dist-packages/pymodbus/client/sync.py", line 108, in execute
return self.execute(request)
File "/usr/local/lib/python3.5/dist-packages/pymodbus/client/common.py", line 114, in read_holding_registers
address, number_of_addresses, **kwargs)
File "/var/www/html/openWB/packages/modules/common/modbus.py", line 87, in __read_registers
Traceback (most recent call last):
2022-06-02 07:59:53: PID: 2464: soc.modules.common.fault_state: Victron Speicher: FaultState FaultStateLevel.ERROR, FaultStr modules.common.modbus <class 'struct.error'> required argument is not an integer, Traceback:
2022-06-02 07:59:53: PID: 2464: soc.modules.common.component_context: Update Komponente ['Victron Speicher']
2022-06-02 07:59:53: PID: 2464: modules.victron.device: Start device reading {'componentNone': <modules.victron.bat.VictronBat object at 0x74e4faf0>}
2022-06-02 07:59:53: PID: 2464: modules.victron.device: Victron MPPT: None
2022-06-02 07:59:53: PID: 2464: modules.victron.device: Victron Modbus-ID: None
2022-06-02 07:59:53: PID: 2464: modules.victron.device: Victron Energy Meter: False
2022-06-02 07:59:53: PID: 2464: modules.victron.device: Victron IP-Adresse: 192.168.178.46
2022-06-02 07:59:53: PID: 2464: legacy run server: Received command ["modules.victron.device","bat","192.168.178.46"]
2022-06-02 07:59:53: PID: 2464: legacy run server: Completed running command in 0.03s: ["modules.victron.device","inverter","192.168.178.46","100","1","0","1"]
2022-06-02 07:59:53: PID: 2464: soc.modules.common.store._api: Saving InverterState(power=-1929, counter=831714.1919180485, currents=[0.0, 0.0, 0.0])
2022-06-02 07:59:53: PID: 2464: modules.common.simcount: simcount Zwischenergebnisse aktuelle Berechnung: Import: 1814 Export: 2994171090.904975 Leistung: -1929
2022-06-02 07:59:53: PID: 2464: modules.common.simcount: simcount Ergebnis: Bezug[Wh]: 0.5038888888888889, Einspeisung[Wh]: 831714.1919180485
2022-06-02 07:59:53: PID: 2464: modules.common.simcount: simcount aufsummierte Energie: Bezug[Ws]: 1814, Einspeisung[Ws]: 2994171090.904975
2022-06-02 07:59:53: PID: 2464: modules.common.simcount: simcount Gesamtenergie im Zeitintervall: -19264.90497469902
2022-06-02 07:59:53: PID: 2464: modules.common.simcount: simcount Berechnungsgrundlage: vergangene Zeit [s]9.90483546257019, vorherige Leistung[W]: -1961, aktuelle Leistung[W]: -1929
2022-06-02 07:59:53: PID: 2464: modules.common.simcount: simcount Zwischenergebnisse letzte Berechnung: Import: 1814 Export: 2994151826 Leistung: -1961
2022-06-02 07:59:53: PID: 2464: soc.modules.common.component_context: Update Komponente ['Victron Wechselrichter']
2022-06-02 07:59:53: PID: 2464: modules.victron.device: Start device reading {'component1': <modules.victron.inverter.VictronInverter object at 0x74e79d30>}
2022-06-02 07:59:53: PID: 2464: modules.victron.device: Victron MPPT: 0
2022-06-02 07:59:53: PID: 2464: modules.victron.device: Victron Modbus-ID: 100
2022-06-02 07:59:53: PID: 2464: modules.victron.device: Victron Energy Meter: True
2022-06-02 07:59:53: PID: 2464: modules.victron.device: Victron IP-Adresse: 192.168.178.46
2022-06-02 07:59:53: PID: 2464: legacy run server: Received command ["modules.victron.device","inverter","192.168.178.46","100","1","0","1"]
2022-06-02 07:59:44: PID: 2464: legacy run server: Completed running command in 0.05s: ["modules.victron.device","counter","192.168.178.46","30","1"]
2022-06-02 07:59:44: PID: 2464: soc.modules.common.store._api: Saving CounterState(power=-565, exported=3866874.046103716, currents=[1.6, -2.2, -2.0], voltages=[233.2, 234.4, 233.5], powers=[341, -485, -421], frequency=50, power_factors=[0.0, 0.0, 0.0], imported=65811.31137992539)
2022-06-02 07:59:44: PID: 2464: modules.common.simcount: simcount Zwischenergebnisse aktuelle Berechnung: Import: 236920720.9677314 Export: 13920746565.973377 Leistung: -565
2022-06-02 07:59:44: PID: 2464: modules.common.simcount: simcount Ergebnis: Bezug[Wh]: 65811.31137992539, Einspeisung[Wh]: 3866874.046103716
2022-06-02 07:59:44: PID: 2464: modules.common.simcount: simcount aufsummierte Energie: Bezug[Ws]: 236920720.9677314, Einspeisung[Ws]: 13920746565.973377
2022-06-02 07:59:44: PID: 2464: modules.common.simcount: simcount exportierte Energie im Zeitintervall: -2144.9733778477666
2022-06-02 07:59:44: PID: 2464: modules.common.simcount: simcount Gesamtenergie im Zeitintervall: -1910.0056464672089
2022-06-02 07:59:44: PID: 2464: modules.common.simcount: simcount Berechnungsgrundlage: vergangene Zeit [s]10.105849981307983, vorherige Leistung[W]: 187, aktuelle Leistung[W]: -565
2022-06-02 07:59:44: PID: 2464: modules.common.simcount: simcount Zwischenergebnisse letzte Berechnung: Import: 236920486 Export: 13920744421 Leistung: 187
2022-06-02 07:59:44: PID: 2464: soc.modules.common.component_context: Update Komponente ['Victron Zähler']
2022-06-02 07:59:44: PID: 2464: modules.victron.device: Start device reading {'componentNone': <modules.victron.counter.VictronCounter object at 0x73cda2f0>}
2022-06-02 07:59:44: PID: 2464: modules.victron.device: Victron MPPT: None
2022-06-02 07:59:44: PID: 2464: modules.victron.device: Victron Modbus-ID: 30
2022-06-02 07:59:44: PID: 2464: modules.victron.device: Victron Energy Meter: True
2022-06-02 07:59:44: PID: 2464: modules.victron.device: Victron IP-Adresse: 192.168.178.46
2022-06-02 07:59:44: PID: 2464: legacy run server: Received command ["modules.victron.device","counter","192.168.178.46","30","1"]
2022-06-02 07:59:43: PID: 2464: legacy run server: Completed running command in 0.02s: ["modules.victron.device","bat","192.168.178.46"]

modules.common.fault_state.FaultState: ("modules.common.modbus <class 'struct.error'> required argument is not an integer", <FaultStateLevel.ERROR: 2>)
str(e)) from e
File "/var/www/html/openWB/packages/modules/common/modbus.py", line 105, in __read_registers
self.delegate.read_holding_registers, address, types, byteorder, wordorder, **kwargs
File "/var/www/html/openWB/packages/modules/common/modbus.py", line 123, in read_holding_registers
power = self.__tcp_client.read_holding_registers(842, ModbusDataType.INT_16, unit=modbus_id)
File "/var/www/html/openWB/packages/modules/victron/bat.py", line 34, in update
self.components[component].update()
File "/var/www/html/openWB/packages/modules/victron/device.py", line 60, in update
Traceback (most recent call last):

The above exception was the direct cause of the following exception:

struct.error: required argument is not an integer
message.function_code)
File "/usr/local/lib/python3.5/dist-packages/pymodbus/framer/socket_framer.py", line 212, in buildPacket
packet = self.client.framer.buildPacket(packet)
File "/usr/local/lib/python3.5/dist-packages/pymodbus/transaction.py", line 228, in _transact
broadcast=broadcast
File "/usr/local/lib/python3.5/dist-packages/pymodbus/transaction.py", line 158, in execute
return self.transaction.execute(request)
File "/usr/local/lib/python3.5/dist-packages/pymodbus/client/sync.py", line 108, in execute
return self.execute(request)
File "/usr/local/lib/python3.5/dist-packages/pymodbus/client/common.py", line 114, in read_holding_registers
address, number_of_addresses, **kwargs)
File "/var/www/html/openWB/packages/modules/common/modbus.py", line 87, in __read_registers
Traceback (most recent call last):
2022-06-02 07:59:43: PID: 2464: soc.modules.common.fault_state: Victron Speicher: FaultState FaultStateLevel.ERROR, FaultStr modules.common.modbus <class 'struct.error'> required argument is not an integer, Traceback:
2022-06-02 07:59:43: PID: 2464: soc.modules.common.component_context: Update Komponente ['Victron Speicher']
2022-06-02 07:59:43: PID: 2464: modules.victron.device: Start device reading {'componentNone': <modules.victron.bat.VictronBat object at 0x74e766b0>}
2022-06-02 07:59:43: PID: 2464: modules.victron.device: Victron MPPT: None
2022-06-02 07:59:43: PID: 2464: modules.victron.device: Victron Modbus-ID: None
2022-06-02 07:59:43: PID: 2464: modules.victron.device: Victron Energy Meter: False
2022-06-02 07:59:43: PID: 2464: modules.victron.device: Victron IP-Adresse: 192.168.178.46
2022-06-02 07:59:43: PID: 2464: legacy run server: Received command ["modules.victron.device","bat","192.168.178.46"]
2022-06-02 07:59:43: PID: 2464: legacy run server: Completed running command in 0.05s: ["modules.victron.device","inverter","192.168.178.46","100","1","0","1"]
2022-06-02 07:59:43: PID: 2464: soc.modules.common.store._api: Saving InverterState(power=-1961, counter=831708.8406602378, currents=[0.0, 0.0, 0.0])
2022-06-02 07:59:43: PID: 2464: modules.common.simcount: simcount Zwischenergebnisse aktuelle Berechnung: Import: 1814 Export: 2994151826.3768563 Leistung: -1961
2022-06-02 07:59:43: PID: 2464: modules.common.simcount: simcount Ergebnis: Bezug[Wh]: 0.5038888888888889, Einspeisung[Wh]: 831708.8406602378
2022-06-02 07:59:43: PID: 2464: modules.common.simcount: simcount aufsummierte Energie: Bezug[Ws]: 1814, Einspeisung[Ws]: 2994151826.3768563
2022-06-02 07:59:43: PID: 2464: modules.common.simcount: simcount Gesamtenergie im Zeitintervall: -19732.376856207848
2022-06-02 07:59:43: PID: 2464: modules.common.simcount: simcount Berechnungsgrundlage: vergangene Zeit [s]9.998670816421509, vorherige Leistung[W]: -1986, aktuelle Leistung[W]: -1961
2022-06-02 07:59:43: PID: 2464: modules.common.simcount: simcount Zwischenergebnisse letzte Berechnung: Import: 1814 Export: 2994132094 Leistung: -1986
2022-06-02 07:59:43: PID: 2464: soc.modules.common.component_context: Update Komponente ['Victron Wechselrichter']
2022-06-02 07:59:43: PID: 2464: modules.victron.device: Start device reading {'component1': <modules.victron.inverter.VictronInverter object at 0x73cda9d0>}
2022-06-02 07:59:43: PID: 2464: modules.victron.device: Victron MPPT: 0
2022-06-02 07:59:43: PID: 2464: modules.victron.device: Victron Modbus-ID: 100
2022-06-02 07:59:43: PID: 2464: modules.victron.device: Victron Energy Meter: True
2022-06-02 07:59:43: PID: 2464: modules.victron.device: Victron IP-Adresse: 192.168.178.46
2022-06-02 07:59:43: PID: 2464: legacy run server: Received command ["modules.victron.device","inverter","192.168.178.46","100","1","0","1"]
2022-06-02 07:59:34: PID: 2464: legacy run server: Completed running command in 0.06s: ["modules.victron.device","counter","192.168.178.46","30","1"]
2022-06-02 07:59:34: PID: 2464: soc.modules.common.store._api: Saving CounterState(power=187, exported=3866873.4505475974, currents=[1.6, -2.2, 2.1], voltages=[233.4, 234.6, 233.1], powers=[336, -493, 344], frequency=50, power_factors=[0.0, 0.0, 0.0], imported=65811.24627015107)
2022-06-02 07:59:34: PID: 2464: modules.common.simcount: simcount Zwischenergebnisse aktuelle Berechnung: Import: 236920486.57254383 Export: 13920744421.97135 Leistung: 187
2022-06-02 07:59:34: PID: 2464: modules.common.simcount: simcount Ergebnis: Bezug[Wh]: 65811.24627015107, Einspeisung[Wh]: 3866873.4505475974
2022-06-02 07:59:34: PID: 2464: modules.common.simcount: simcount aufsummierte Energie: Bezug[Ws]: 236920486.57254383, Einspeisung[Ws]: 13920744421.97135
2022-06-02 07:59:34: PID: 2464: modules.common.simcount: simcount exportierte Energie im Zeitintervall: -2419.9713496904433
2022-06-02 07:59:34: PID: 2464: modules.common.simcount: simcount Gesamtenergie im Zeitintervall: -2205.3988058567047
2022-06-02 07:59:34: PID: 2464: modules.common.simcount: simcount Berechnungsgrundlage: vergangene Zeit [s]10.001808643341064, vorherige Leistung[W]: -628, aktuelle Leistung[W]: 187
2022-06-02 07:59:34: PID: 2464: modules.common.simcount: simcount Zwischenergebnisse letzte Berechnung: Import: 236920272 Export: 13920742002 Leistung: -628
2022-06-02 07:59:34: PID: 2464: soc.modules.common.component_context: Update Komponente ['Victron Zähler']
2022-06-02 07:59:34: PID: 2464: modules.victron.device: Start device reading {'componentNone': <modules.victron.counter.VictronCounter object at 0x74e79250>}
2022-06-02 07:59:34: PID: 2464: modules.victron.device: Victron MPPT: None
2022-06-02 07:59:34: PID: 2464: modules.victron.device: Victron Modbus-ID: 30
2022-06-02 07:59:34: PID: 2464: modules.victron.device: Victron Energy Meter: True
2022-06-02 07:59:34: PID: 2464: modules.victron.device: Victron IP-Adresse: 192.168.178.46
2022-06-02 07:59:34: PID: 2464: legacy run server: Received command ["modules.victron.device","counter","192.168.178.46","30","1"]
2022-06-02 07:59:33: PID: 2464: legacy run server: Completed running command in 0.02s: ["modules.victron.device","bat","192.168.178.46"]

modules.common.fault_state.FaultState: ("modules.common.modbus <class 'struct.error'> required argument is not an integer", <FaultStateLevel.ERROR: 2>)
str(e)) from e
File "/var/www/html/openWB/packages/modules/common/modbus.py", line 105, in __read_registers
self.delegate.read_holding_registers, address, types, byteorder, wordorder, **kwargs
File "/var/www/html/openWB/packages/modules/common/modbus.py", line 123, in read_holding_registers
power = self.__tcp_client.read_holding_registers(842, ModbusDataType.INT_16, unit=modbus_id)
File "/var/www/html/openWB/packages/modules/victron/bat.py", line 34, in update
self.components[component].update()
File "/var/www/html/openWB/packages/modules/victron/device.py", line 60, in update
Traceback (most recent call last):

The above exception was the direct cause of the following exception:

struct.error: required argument is not an integer
message.function_code)
File "/usr/local/lib/python3.5/dist-packages/pymodbus/framer/socket_framer.py", line 212, in buildPacket
packet = self.client.framer.buildPacket(packet)
File "/usr/local/lib/python3.5/dist-packages/pymodbus/transaction.py", line 228, in _transact
broadcast=broadcast
File "/usr/local/lib/python3.5/dist-packages/pymodbus/transaction.py", line 158, in execute
return self.transaction.execute(request)
File "/usr/local/lib/python3.5/dist-packages/pymodbus/client/sync.py", line 108, in execute
return self.execute(request)
File "/usr/local/lib/python3.5/dist-packages/pymodbus/client/common.py", line 114, in read_holding_registers
address, number_of_addresses, **kwargs)
File "/var/www/html/openWB/packages/modules/common/modbus.py", line 87, in __read_registers
Traceback (most recent call last):
2022-06-02 07:59:33: PID: 2464: soc.modules.common.fault_state: Victron Speicher: FaultState FaultStateLevel.ERROR, FaultStr modules.common.modbus <class 'struct.error'> required argument is not an integer, Traceback:
2022-06-02 07:59:33: PID: 2464: soc.modules.common.component_context: Update Komponente ['Victron Speicher']
2022-06-02 07:59:33: PID: 2464: modules.victron.device: Start device reading {'componentNone': <modules.victron.bat.VictronBat object at 0x73cecd90>}
2022-06-02 07:59:33: PID: 2464: modules.victron.device: Victron MPPT: None
2022-06-02 07:59:33: PID: 2464: modules.victron.device: Victron Modbus-ID: None
2022-06-02 07:59:33: PID: 2464: modules.victron.device: Victron Energy Meter: False
2022-06-02 07:59:33: PID: 2464: modules.victron.device: Victron IP-Adresse: 192.168.178.46
2022-06-02 07:59:33: PID: 2464: legacy run server: Received command ["modules.victron.device","bat","192.168.178.46"]
2022-06-02 07:59:33: PID: 2464: legacy run server: Completed running command in 0.03s: ["modules.victron.device","inverter","192.168.178.46","100","1","0","1"]
2022-06-02 07:59:33: PID: 2464: soc.modules.common.store._api: Saving InverterState(power=-1986, counter=831703.3594476652, currents=[0.0, 0.0, 0.0])
2022-06-02 07:59:33: PID: 2464: modules.common.simcount: simcount Zwischenergebnisse aktuelle Berechnung: Import: 1814 Export: 2994132094.011595 Leistung: -1986
2022-06-02 07:59:33: PID: 2464: modules.common.simcount: simcount Ergebnis: Bezug[Wh]: 0.5038888888888889, Einspeisung[Wh]: 831703.3594476652
2022-06-02 07:59:33: PID: 2464: modules.common.simcount: simcount aufsummierte Energie: Bezug[Ws]: 1814, Einspeisung[Ws]: 2994132094.011595
2022-06-02 07:59:33: PID: 2464: modules.common.simcount: simcount Gesamtenergie im Zeitintervall: -19834.01159477234
2022-06-02 07:59:33: PID: 2464: modules.common.simcount: simcount Berechnungsgrundlage: vergangene Zeit [s]9.964336395263672, vorherige Leistung[W]: -1995, aktuelle Leistung[W]: -1986
2022-06-02 07:59:33: PID: 2464: modules.common.simcount: simcount Zwischenergebnisse letzte Berechnung: Import: 1814 Export: 2994112260 Leistung: -1995
2022-06-02 07:59:33: PID: 2464: soc.modules.common.component_context: Update Komponente ['Victron Wechselrichter']
2022-06-02 07:59:33: PID: 2464: modules.victron.device: Start device reading {'component1': <modules.victron.inverter.VictronInverter object at 0x73cce910>}
2022-06-02 07:59:33: PID: 2464: modules.victron.device: Victron MPPT: 0
2022-06-02 07:59:33: PID: 2464: modules.victron.device: Victron Modbus-ID: 100
2022-06-02 07:59:33: PID: 2464: modules.victron.device: Victron Energy Meter: True
2022-06-02 07:59:33: PID: 2464: modules.victron.device: Victron IP-Adresse: 192.168.178.46
2022-06-02 07:59:33: PID: 2464: legacy run server: Received command ["modules.victron.device","inverter","192.168.178.46","100","1","0","1"]
2022-06-02 07:59:24: PID: 2464: legacy run server: Completed running command in 0.06s: ["modules.victron.device","counter","192.168.178.46","30","1"]
2022-06-02 07:59:24: PID: 2464: soc.modules.common.store._api: Saving CounterState(power=-628, exported=3866872.778414066, currents=[1.6, -2.2, -2.2], voltages=[233.5, 234.6, 233.6], powers=[343, -497, -474], frequency=50, power_factors=[0.0, 0.0, 0.0], imported=65811.18666666666)
2022-06-02 07:59:24: PID: 2464: modules.common.simcount: simcount Zwischenergebnisse aktuelle Berechnung: Import: 236920272 Export: 13920742002.290638 Leistung: -628
2022-06-02 07:59:24: PID: 2464: modules.common.simcount: simcount Ergebnis: Bezug[Wh]: 65811.18666666666, Einspeisung[Wh]: 3866872.778414066
2022-06-02 07:59:24: PID: 2464: modules.common.simcount: simcount aufsummierte Energie: Bezug[Ws]: 236920272, Einspeisung[Ws]: 13920742002.290638
2022-06-02 07:59:24: PID: 2464: modules.common.simcount: simcount Gesamtenergie im Zeitintervall: -6167.290637373924
2022-06-02 07:59:24: PID: 2464: modules.common.simcount: simcount Berechnungsgrundlage: vergangene Zeit [s]9.891404390335083, vorherige Leistung[W]: -619, aktuelle Leistung[W]: -628
2022-06-02 07:59:24: PID: 2464: modules.common.simcount: simcount Zwischenergebnisse letzte Berechnung: Import: 236920272 Export: 13920735835 Leistung: -619
2022-06-02 07:59:24: PID: 2464: soc.modules.common.component_context: Update Komponente ['Victron Zähler']
2022-06-02 07:59:24: PID: 2464: modules.victron.device: Start device reading {'componentNone': <modules.victron.counter.VictronCounter object at 0x74e75ab0>}
2022-06-02 07:59:24: PID: 2464: modules.victron.device: Victron MPPT: None
2022-06-02 07:59:24: PID: 2464: modules.victron.device: Victron Modbus-ID: 30
2022-06-02 07:59:24: PID: 2464: modules.victron.device: Victron Energy Meter: True
2022-06-02 07:59:24: PID: 2464: modules.victron.device: Victron IP-Adresse: 192.168.178.46
2022-06-02 07:59:24: PID: 2464: legacy run server: Received command ["modules.victron.device","counter","192.168.178.46","30","1"]
2022-06-02 07:59:23: PID: 2464: legacy run server: Completed running command in 0.03s: ["modules.victron.device","bat","192.168.178.46"]

modules.common.fault_state.FaultState: ("modules.common.modbus <class 'struct.error'> required argument is not an integer", <FaultStateLevel.ERROR: 2>)
str(e)) from e
File "/var/www/html/openWB/packages/modules/common/modbus.py", line 105, in __read_registers
self.delegate.read_holding_registers, address, types, byteorder, wordorder, **kwargs
File "/var/www/html/openWB/packages/modules/common/modbus.py", line 123, in read_holding_registers
power = self.__tcp_client.read_holding_registers(842, ModbusDataType.INT_16, unit=modbus_id)
File "/var/www/html/openWB/packages/modules/victron/bat.py", line 34, in update
self.components[component].update()
File "/var/www/html/openWB/packages/modules/victron/device.py", line 60, in update
Traceback (most recent call last):

The above exception was the direct cause of the following exception:

struct.error: required argument is not an integer
message.function_code)
File "/usr/local/lib/python3.5/dist-packages/pymodbus/framer/socket_framer.py", line 212, in buildPacket
packet = self.client.framer.buildPacket(packet)
File "/usr/local/lib/python3.5/dist-packages/pymodbus/transaction.py", line 228, in _transact
broadcast=broadcast
File "/usr/local/lib/python3.5/dist-packages/pymodbus/transaction.py", line 158, in execute
return self.transaction.execute(request)
File "/usr/local/lib/python3.5/dist-packages/pymodbus/client/sync.py", line 108, in execute
return self.execute(request)
File "/usr/local/lib/python3.5/dist-packages/pymodbus/client/common.py", line 114, in read_holding_registers
address, number_of_addresses, **kwargs)
File "/var/www/html/openWB/packages/modules/common/modbus.py", line 87, in __read_registers
Traceback (most recent call last):
2022-06-02 07:59:23: PID: 2464: soc.modules.common.fault_state: Victron Speicher: FaultState FaultStateLevel.ERROR, FaultStr modules.common.modbus <class 'struct.error'> required argument is not an integer, Traceback:
2022-06-02 07:59:23: PID: 2464: soc.modules.common.component_context: Update Komponente ['Victron Speicher']
2022-06-02 07:59:23: PID: 2464: modules.victron.device: Start device reading {'componentNone': <modules.victron.bat.VictronBat object at 0x73cbf710>}
2022-06-02 07:59:23: PID: 2464: modules.victron.device: Victron MPPT: None
2022-06-02 07:59:23: PID: 2464: modules.victron.device: Victron Modbus-ID: None
2022-06-02 07:59:23: PID: 2464: modules.victron.device: Victron Energy Meter: False
2022-06-02 07:59:23: PID: 2464: modules.victron.device: Victron IP-Adresse: 192.168.178.46
2022-06-02 07:59:23: PID: 2464: legacy run server: Received command ["modules.victron.device","bat","192.168.178.46"]
2022-06-02 07:59:23: PID: 2464: legacy run server: Completed running command in 0.06s: ["modules.victron.device","inverter","192.168.178.46","100","1","0","1"]
2022-06-02 07:59:23: PID: 2464: soc.modules.common.store._api: Saving InverterState(power=-1995, counter=831697.8501814982, currents=[0.0, 0.0, 0.0])
2022-06-02 07:59:23: PID: 2464: modules.common.simcount: simcount Zwischenergebnisse aktuelle Berechnung: Import: 1814 Export: 2994112260.6533937 Leistung: -1995
2022-06-02 07:59:23: PID: 2464: modules.common.simcount: simcount Ergebnis: Bezug[Wh]: 0.5038888888888889, Einspeisung[Wh]: 831697.8501814982
2022-06-02 07:59:23: PID: 2464: modules.common.simcount: simcount aufsummierte Energie: Bezug[Ws]: 1814, Einspeisung[Ws]: 2994112260.6533937
2022-06-02 07:59:23: PID: 2464: modules.common.simcount: simcount Gesamtenergie im Zeitintervall: -20270.653393507004
2022-06-02 07:59:23: PID: 2464: modules.common.simcount: simcount Berechnungsgrundlage: vergangene Zeit [s]10.099976778030396, vorherige Leistung[W]: -2019, aktuelle Leistung[W]: -1995
2022-06-02 07:59:23: PID: 2464: modules.common.simcount: simcount Zwischenergebnisse letzte Berechnung: Import: 1814 Export: 2994091990 Leistung: -2019
2022-06-02 07:59:23: PID: 2464: soc.modules.common.component_context: Update Komponente ['Victron Wechselrichter']
2022-06-02 07:59:23: PID: 2464: modules.victron.device: Start device reading {'component1': <modules.victron.inverter.VictronInverter object at 0x73cc5f90>}
2022-06-02 07:59:23: PID: 2464: modules.victron.device: Victron MPPT: 0
2022-06-02 07:59:23: PID: 2464: modules.victron.device: Victron Modbus-ID: 100
2022-06-02 07:59:23: PID: 2464: modules.victron.device: Victron Energy Meter: True
2022-06-02 07:59:23: PID: 2464: modules.victron.device: Victron IP-Adresse: 192.168.178.46
2022-06-02 07:59:23: PID: 2464: legacy run server: Received command ["modules.victron.device","inverter","192.168.178.46","100","1","0","1"]
2022-06-02 07:59:14: PID: 2464: legacy run server: Completed running command in 0.10s: ["modules.victron.device","counter","192.168.178.46","30","1"]
2022-06-02 07:59:14: PID: 2464: soc.modules.common.store._api: Saving CounterState(power=-619, exported=3866871.0653482364, currents=[1.7, -2.2, -2.2], voltages=[233.7, 234.9, 234.0], powers=[362, -502, -479], frequency=50, power_factors=[0.0, 0.0, 0.0], imported=65811.18666666666)
2022-06-02 07:59:14: PID: 2464: modules.common.simcount: simcount Zwischenergebnisse aktuelle Berechnung: Import: 236920272 Export: 13920735835.25365 Leistung: -619
2022-06-02 07:59:14: PID: 2464: modules.common.simcount: simcount Ergebnis: Bezug[Wh]: 65811.18666666666, Einspeisung[Wh]: 3866871.0653482364
2022-06-02 07:59:14: PID: 2464: modules.common.simcount: simcount aufsummierte Energie: Bezug[Ws]: 236920272, Einspeisung[Ws]: 13920735835.25365
2022-06-02 07:59:14: PID: 2464: modules.common.simcount: simcount Gesamtenergie im Zeitintervall: -6165.25365114212
2022-06-02 07:59:14: PID: 2464: modules.common.simcount: simcount Berechnungsgrundlage: vergangene Zeit [s]10.024802684783936, vorherige Leistung[W]: -611, aktuelle Leistung[W]: -619
2022-06-02 07:59:14: PID: 2464: modules.common.simcount: simcount Zwischenergebnisse letzte Berechnung: Import: 236920272 Export: 13920729670 Leistung: -611
2022-06-02 07:59:14: PID: 2464: soc.modules.common.component_context: Update Komponente ['Victron Zähler']
2022-06-02 07:59:14: PID: 2464: modules.victron.device: Start device reading {'componentNone': <modules.victron.counter.VictronCounter object at 0x73cce710>}
2022-06-02 07:59:14: PID: 2464: modules.victron.device: Victron MPPT: None
2022-06-02 07:59:14: PID: 2464: modules.victron.device: Victron Modbus-ID: 30
2022-06-02 07:59:14: PID: 2464: modules.victron.device: Victron Energy Meter: True
2022-06-02 07:59:14: PID: 2464: modules.victron.device: Victron IP-Adresse: 192.168.178.46
2022-06-02 07:59:14: PID: 2464: legacy run server: Received command ["modules.victron.device","counter","192.168.178.46","30","1"]
2022-06-02 07:59:13: PID: 2464: legacy run server: Completed running command in 0.03s: ["modules.victron.device","bat","192.168.178.46"]
Jan
Beiträge: 21
Registriert: Do Nov 26, 2020 10:10 am

Re: Rückmeldungen Beta 1.9.267

Beitrag von Jan »

LutzB hat geschrieben: Mo Mai 30, 2022 5:39 am Ja, der Hi5/10 spricht direkt Modbus/TCP.
Das gilt aber nur für den Smile Hi5/10, nicht für die Vorgänger Smile 5?

Schöne Grüße,
Jan
LutzB
Beiträge: 3522
Registriert: Di Feb 25, 2020 9:23 am

Re: Rückmeldungen Beta 1.9.267

Beitrag von LutzB »

Victron Speicher sollten jetzt in der Nightly wieder gehen.
LutzB
Beiträge: 3522
Registriert: Di Feb 25, 2020 9:23 am

Re: Rückmeldungen Beta 1.9.267

Beitrag von LutzB »

Jan hat geschrieben: Do Jun 02, 2022 9:16 pm
LutzB hat geschrieben: Mo Mai 30, 2022 5:39 am Ja, der Hi5/10 spricht direkt Modbus/TCP.
Das gilt aber nur für den Smile Hi5/10, nicht für die Vorgänger Smile 5?

Schöne Grüße,
Jan
Das kann Dir wohl nur Alpha sagen.
ama
Beiträge: 70
Registriert: So Okt 14, 2018 7:38 pm

Re: Rückmeldungen Beta 1.9.267

Beitrag von ama »

Victron Speichermodul funktioniert mit der geänderten Nightly 1.9.268 jetzt wieder - DANKE!!
Gesperrt